rcdallas
post Feb 6 2010, 10:36 AM
Post #1


Ground Hand
Group Icon

Group: Members
Posts: 68
Joined: 11-May 07
From: Texas
Member No.: 4947
Industry: Power
Union: IBEW Local 69



Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.



--------------------
E * I = P
Go to the top of the page
 
+Quote Post
olo131
post Feb 6 2010, 10:52 AM
Post #2


CATV is my life
Group Icon

Group: Moderator Group
Posts: 2045
Joined: 24-January 09
From: Panama City Beach, Fl
Member No.: 7790
Industry: CATV
Union: no



Come on Power guys this should be easy for you. Don't let a Cable Guy be right.

I guess....... you move the oscillating knibbling pin to the third phase shifting connector......

Just having fun... I would love to see some real guesses.

Thanks for the post
olo131


--------------------
"To err is human but to really screw up you need a computer"

Go to the top of the page
 
+Quote Post
wood stabber
post Feb 6 2010, 05:58 PM
Post #3


Lead Man
Group Icon

Group: Members
Posts: 196
Joined: 25-December 08
From: nor cal
Member No.: 7474
Industry: Power
Union: IBEW 1245 Journeyman Power Lineman



QUOTE (rcdallas @ Feb 6 2010, 10:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.


Why did you ground X3?That causes a phase to ground.... If I wanted 240v I would've used X1 and X3 and left X2 alone...
And lastly...if you OPEN the pot ,how you gonna check voltage? I guess if you had backfeed you get a reading on you volt meter,but that's not telling you if your pots good or not!
Go to the top of the page
 
+Quote Post
rcdallas
post Feb 6 2010, 08:35 PM
Post #4


Ground Hand
Group Icon

Group: Members
Posts: 68
Joined: 11-May 07
From: Texas
Member No.: 4947
Industry: Power
Union: IBEW Local 69



QUOTE (wood stabber @ Feb 6 2010, 06:58 PM) *
QUOTE (rcdallas @ Feb 6 2010, 10:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.


Why did you ground X3?That causes a phase to ground.... If I wanted 240v I would've used X1 and X3 and left X2 alone...
And lastly...if you OPEN the pot ,how you gonna check voltage? I guess if you had backfeed you get a reading on you volt meter,but that's not telling you if your pots good or not!


You ground the X3 or X1 so that you get straight 240... it'll give you a 240 hot leg to ground... we use that configuration on our street light circuits...

If you open the breaker on a CSP in this type of configuration you'll end up with primary voltage due to the physical design of the CSP loosing a reference to ground with the ground strap not being on the X2 bushing.



--------------------
E * I = P
Go to the top of the page
 
+Quote Post
wood stabber
post Feb 7 2010, 08:29 AM
Post #5


Lead Man
Group Icon

Group: Members
Posts: 196
Joined: 25-December 08
From: nor cal
Member No.: 7474
Industry: Power
Union: IBEW 1245 Journeyman Power Lineman



QUOTE (rcdallas @ Feb 6 2010, 08:35 PM) *
QUOTE (wood stabber @ Feb 6 2010, 06:58 PM) *
QUOTE (rcdallas @ Feb 6 2010, 10:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.


Why did you ground X3?That causes a phase to ground.... If I wanted 240v I would've used X1 and X3 and left X2 alone...
And lastly...if you OPEN the pot ,how you gonna check voltage? I guess if you had backfeed you get a reading on you volt meter,but that's not telling you if your pots good or not!


You ground the X3 or X1 so that you get straight 240... it'll give you a 240 hot leg to ground... we use that configuration on our street light circuits...

If you open the breaker on a CSP in this type of configuration you'll end up with primary voltage due to the physical design of the CSP loosing a reference to ground with the ground strap not being on the X2 bushing.


Thanks,that's nice to know,you don't see to many CSP's out here in Cali,they have been changing them out to conventionals for a long time, pull the doors,drop the pot,hang a new pot,plug it in.
So when you say you will get primary voltage,are you meaning the secondary side will read primary voltage ?
Go to the top of the page
 
+Quote Post
strange052
post Feb 7 2010, 04:08 PM
Post #6


Fallen Never Forgotten, Support our Troops
Group Icon

Group: Moderator Group
Posts: 3129
Joined: 25-July 06
Member No.: 2241
Industry: Telephone
Union: TWU 202



QUOTE (rcdallas @ Feb 6 2010, 11:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.



I call over to the local POWER yard and offer to buy one of them a case of beer for hoooking it up for me, because Im just a phone guy that dont know sh*t about power


--------------------
There may be old Linemen, There may be careless Linemen. There are however, no old, careless Linemen!


THANK A SOLDIER
Go to the top of the page
 
+Quote Post
System Tech Seni...
post Feb 7 2010, 04:14 PM
Post #7


Line-God
Group Icon

Group: Moderator Group
Posts: 2023
Joined: 29-October 09
From: Clarksville, TN
Member No.: 10276
Industry: CATV
Union: No



LOL@ Strange


--------------------
Jason C.
System Technician Senior
Charter Communications
Clarksville, TN


Go to the top of the page
 
+Quote Post
olo131
post Feb 7 2010, 04:16 PM
Post #8


CATV is my life
Group Icon

Group: Moderator Group
Posts: 2045
Joined: 24-January 09
From: Panama City Beach, Fl
Member No.: 7790
Industry: CATV
Union: no



Well Strange you could have still given a guess you know as much as I do when it comes to Power and I gave it a go!!!!

Hell LRod didn't even guess and he said he reads every post....... Maybe he will need to hit the books...... devil-smiley-024[1].gif

olo131


--------------------
"To err is human but to really screw up you need a computer"

Go to the top of the page
 
+Quote Post
System Tech Seni...
post Feb 7 2010, 04:23 PM
Post #9


Line-God
Group Icon

Group: Moderator Group
Posts: 2023
Joined: 29-October 09
From: Clarksville, TN
Member No.: 10276
Industry: CATV
Union: No



I'm gonna go with nothing since it's open. :)


--------------------
Jason C.
System Technician Senior
Charter Communications
Clarksville, TN


Go to the top of the page
 
+Quote Post
Lightningrod
post Feb 7 2010, 04:52 PM
Post #10


Line-God
Group Icon

Group: Moderator Group
Posts: 3005
Joined: 1-February 04
From: New Brunswick, Canada
Member No.: 147
Industry: Power
Union: I.B.E.W. Local 37



QUOTE (wood stabber @ Feb 6 2010, 05:58 PM) *
QUOTE (rcdallas @ Feb 6 2010, 10:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.


Why did you ground X3?That causes a phase to ground.... If I wanted 240v I would've used X1 and X3 and left X2 alone...
And lastly...if you OPEN the pot ,how you gonna check voltage? I guess if you had backfeed you get a reading on you volt meter,but that's not telling you if your pots good or not!


I can see the 240V no problem, you have hot on one end and ground on the other end of you windings as you do with primary as the x3 acts the same as your h2.
Do you know why you get line voltage on the secondary winding, we have alot of 240V streelight circuits on the housing areas of the local military base. I don't know if any CSP's are feeding it though but we still have a few thousand CSP's in our system.


--------------------
Live Safe, Live Long.

lightningrod
Go to the top of the page
 
+Quote Post
olo131
post Feb 7 2010, 05:02 PM
Post #11


CATV is my life
Group Icon

Group: Moderator Group
Posts: 2045
Joined: 24-January 09
From: Panama City Beach, Fl
Member No.: 7790
Industry: CATV
Union: no



QUOTE (olo131 @ Feb 7 2010, 06:16 PM) *
Hell LRod didn't even guess and he said he reads every post....... Maybe he will need to hit the books...... devil-smiley-024[1].gif

olo131

QUOTE (Lightningrod @ Feb 7 2010, 06:52 PM) *
I can see the 240V no problem, you have hot on one end and ground on the other end of you windings as you do with primary as the x3 acts the same as your h2.
Do you know why you get line voltage on the secondary winding, we have alot of 240V streelight circuits on the housing areas of the local military base. I don't know if any CSP's are feeding it though but we still have a few thousand CSP's in our system.



Looks like peer pressure to me!!!!!! devil-smiley-024[1].gif

olo131


--------------------
"To err is human but to really screw up you need a computer"

Go to the top of the page
 
+Quote Post
System Tech Seni...
post Feb 7 2010, 05:06 PM
Post #12


Line-God
Group Icon

Group: Moderator Group
Posts: 2023
Joined: 29-October 09
From: Clarksville, TN
Member No.: 10276
Industry: CATV
Union: No



Do we have an answer yet lol?? I'm kinda curious to know lol.


--------------------
Jason C.
System Technician Senior
Charter Communications
Clarksville, TN


Go to the top of the page
 
+Quote Post
rcdallas
post Feb 7 2010, 09:37 PM
Post #13


Ground Hand
Group Icon

Group: Members
Posts: 68
Joined: 11-May 07
From: Texas
Member No.: 4947
Industry: Power
Union: IBEW Local 69



QUOTE (wood stabber @ Feb 7 2010, 08:29 AM) *
QUOTE (rcdallas @ Feb 6 2010, 08:35 PM) *
QUOTE (wood stabber @ Feb 6 2010, 06:58 PM) *
QUOTE (rcdallas @ Feb 6 2010, 10:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.


Why did you ground X3?That causes a phase to ground.... If I wanted 240v I would've used X1 and X3 and left X2 alone...
And lastly...if you OPEN the pot ,how you gonna check voltage? I guess if you had backfeed you get a reading on you volt meter,but that's not telling you if your pots good or not!


You ground the X3 or X1 so that you get straight 240... it'll give you a 240 hot leg to ground... we use that configuration on our street light circuits...

If you open the breaker on a CSP in this type of configuration you'll end up with primary voltage due to the physical design of the CSP loosing a reference to ground with the ground strap not being on the X2 bushing.


Thanks,that's nice to know,you don't see to many CSP's out here in Cali,they have been changing them out to conventionals for a long time, pull the doors,drop the pot,hang a new pot,plug it in.
So when you say you will get primary voltage,are you meaning the secondary side will read primary voltage ?



Yes... you'll end up with primary voltage out the secondary bushings in that configuration. We don't have many CSP's out here anymore on our system, but you'll come across them every now and then.




--------------------
E * I = P
Go to the top of the page
 
+Quote Post
rcdallas
post Feb 7 2010, 09:46 PM
Post #14


Ground Hand
Group Icon

Group: Members
Posts: 68
Joined: 11-May 07
From: Texas
Member No.: 4947
Industry: Power
Union: IBEW Local 69



QUOTE (Lightningrod @ Feb 7 2010, 04:52 PM) *
QUOTE (wood stabber @ Feb 6 2010, 05:58 PM) *
QUOTE (rcdallas @ Feb 6 2010, 10:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.


Why did you ground X3?That causes a phase to ground.... If I wanted 240v I would've used X1 and X3 and left X2 alone...
And lastly...if you OPEN the pot ,how you gonna check voltage? I guess if you had backfeed you get a reading on you volt meter,but that's not telling you if your pots good or not!


I can see the 240V no problem, you have hot on one end and ground on the other end of you windings as you do with primary as the x3 acts the same as your h2.
Do you know why you get line voltage on the secondary winding, we have alot of 240V streelight circuits on the housing areas of the local military base. I don't know if any CSP's are feeding it though but we still have a few thousand CSP's in our system.



I posted it previously... it's just the physical design of the CSP, when you open the breaker it breaks physical contact between X3 and X1 and X2 stays closed.

We will use the straight 240, and where a photocell/relay is needed for 120 we'll use the 120v to power it, at one time someone was shootin some trouble checking voltage it burned their volt meter up... later on they used phasing sticks and seen there was primary voltage.. thankfully noone hurt.

Some shiznit to think about it.


--------------------
E * I = P
Go to the top of the page
 
+Quote Post
topgroove
post Feb 8 2010, 06:37 AM
Post #15


Lead Man
Group Icon

Group: Members
Posts: 192
Joined: 30-August 05
Member No.: 849
Industry: Power



QUOTE (rcdallas @ Feb 8 2010, 12:46 AM) *
QUOTE (Lightningrod @ Feb 7 2010, 04:52 PM) *
QUOTE (wood stabber @ Feb 6 2010, 05:58 PM) *
QUOTE (rcdallas @ Feb 6 2010, 10:36 AM) *
Ok you got yourself a CSP 120/240 transformer...

Lets say you wanted straight 240, so you move your ground strap to over to x3...

With the breaker closed, you check voltage, x3 to x2, you get 120, x3 to x1 you get 240.

If you open the breaker on this this CSP and check voltage... what do you think your gonna get?

I'll give you a hint, don't do this on a CSP.


Why did you ground X3?That causes a phase to ground.... If I wanted 240v I would've used X1 and X3 and left X2 alone...
And lastly...if you OPEN the pot ,how you gonna check voltage? I guess if you had backfeed you get a reading on you volt meter,but that's not telling you if your pots good or not!


I can see the 240V no problem, you have hot on one end and ground on the other end of you windings as you do with primary as the x3 acts the same as your h2.
Do you know why you get line voltage on the secondary winding, we have alot of 240V streelight circuits on the housing areas of the local military base. I don't know if any CSP's are feeding it though but we still have a few thousand CSP's in our system.



I posted it previously... it's just the physical design of the CSP, when you open the breaker it breaks physical contact between X3 and X1 and X2 stays closed.

We will use the straight 240, and where a photocell/relay is needed for 120 we'll use the 120v to power it, at one time someone was shootin some trouble checking voltage it burned their volt meter up... later on they used phasing sticks and seen there was primary voltage.. thankfully noone hurt.

Some shiznit to think about it.

True... because of the design of a CSP opening the breaker on a CSP does does de-energize the secondary coil but an induced voltage will develop on the coil. It can reach the potential of the primary coil we're talking mili amps though. When using a fluke multimeter you can destroy it(and I have ) by testing across the bushings with the secondary breaker in the open position. Always better to use an ellwood.
To clear thing up on grounding a secondary coil.... A secondary coil can take ONE ground. The transformer could care less if its x1, x2, or x3. When building a straight 240 bank the ground straps are omited. We ground one of the hotlegs in this case. Your phase to phase voltage on any two hotlegs will be 240 but your voltage from the grounded hotleg to ground will of cource be zero.
Go to the top of the page
 
+Quote Post
topgroove
post Feb 8 2010, 10:49 AM
Post #16


Lead Man
Group Icon

Group: Members
Posts: 192
Joined: 30-August 05
Member No.: 849
Industry: Power



QUOTE (System Tech Senior @ Feb 7 2010, 08:06 PM) *
Do we have an answer yet lol?? I'm kinda curious to know lol.
I just answered it two posts ago in this thread.When you open the breaker on a csp an induced voltage will develop on the secondary coil. the voltage can reach the potential of the primary coil. the current produced is in miliamps. not enough to hurt someone but certainly enough to dammage a fluke multimeter.
Go to the top of the page
 
+Quote Post
System Tech Seni...
post Feb 8 2010, 03:29 PM
Post #17


Line-God
Group Icon

Group: Moderator Group
Posts: 2023
Joined: 29-October 09
From: Clarksville, TN
Member No.: 10276
Industry: CATV
Union: No



So when I answered with nothing was I right?


--------------------
Jason C.
System Technician Senior
Charter Communications
Clarksville, TN


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 

Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No new   52 -TexasLineworker- 15108 22nd February 2010 - 08:28 AM
Last post by: Lineman1983
No new   14 linemans lady 1501 12th October 2004 - 06:15 PM
Last post by: Lightningrod
No New Posts   4 linemans lady 503 12th October 2004 - 06:05 PM
Last post by: bulldozer7777
No New Posts   0 linemans lady 309 30th November 2004 - 06:12 PM
Last post by: linemans lady
No New Posts 0 -- 947 19th March 2005 - 09:14 AM
Last post by: -TexasLineworker-





RSS Lo-Fi Version Time is now: 11th March 2010 - 07:50 PM



Design by: Free Skins IPB & eBusiness Chat