Equipotential Grounding.....
#21
Posted 28 May 2004 - 05:21 AM
As for your question, here is my take on it.
Bracket grounding does not provide protection when you are a few spans away from the grounds and the line becomes energized from an operating error or a live conductor making contact. Bracket grounding 2 miles apart will provide protection from induction and backfeed from small generators. Because equipotential grounding is difficult (impractical) when removing old conductor, raising new conductor and during a large planned outage with lots of crews and work on every pole, bracket grounding could provide protection if, extra steps are taken to guarantee that there is virtually no risk of accidental reenergization. This guarantee would need to be planned, written down and approved as an exception to the mandatory equipotential grounding method. Extra measures such as removing a span of conductor, removing loops and risers may need to be taken.
The above would be a procedure violation in many organizations and would need to be approved. The same organizations that do not approve an exception to bracket grounding sometimes allow the high risk practice of taking a line out of service (because the job cannot be done safely live line), not grounding, but treating it alive by using rubber gloves to do the job.
Wayne
#22
Posted 30 May 2004 - 04:53 AM
#23
Posted 30 May 2004 - 11:18 AM
#24
Posted 30 May 2004 - 12:29 PM
This couldn't be farther from the truth.
The entire line is energized at the same time. You could put 100 sets of grounds on and if your'e on the pole working in leathers, and the line comes hot, your'e not protected at all. Your'e only another path to ground.
By using grounds only the only thing you can hope to acomplish is to blow a fuse or trip a breaker. That is if your'e not so far from the sub that it only sees it as load.
By using an equipotential grounding cluster on the pole you are working on, you put yourself at the same potential. You should mount it as close to your feet as possible to assure that you are within the field. It is a pain in the @ss to use, and you have to set it up at every pole and go through the whole procedure of grounding it each time. But I truly believe it will save lives.
Sorry if I talk too much.
#25
Posted 30 May 2004 - 12:46 PM
#26
Posted 30 May 2004 - 12:56 PM
#27
Posted 30 May 2004 - 05:20 PM
Are you having to work this reconductor job off the pole?
I've had to do a few myself. What we did was find some way to kill the old line. Do some switching or take an outage for a bit. Then lay it out and hang the dollys and ropes. Then switch it back if we had to. Keep the new conductor grounded while we strung, and clipped it in. You could set up the equi.potential grounding stuff up while tying it in. In these situations I prefer using conventional tie wires. It's a lot easier to keep control of my tails. Then when everything is bumped over, let the old wire down at the deadends, and take a set of long hot cutters up the pole and cut the old wire at the layout arm. Right at the arm, so that the ends wont flop up into anything.
Of course sometimes there's stuff below that it can't land on so you have to rig up something else. Like a chainsaw or a bulldozer in front of a bucket truck!! yes way
#28
Posted 30 May 2004 - 05:27 PM
#29
Posted 30 May 2004 - 05:36 PM
Just work it all like it's hot. brewsky
#30
Posted 30 May 2004 - 05:39 PM
#31 Guest_TexasLineworker_*
Posted 30 May 2004 - 10:18 PM
#32
Posted 31 May 2004 - 08:01 AM
"Bracket grounding does not provide protection when you are a few spans away from the grounds and the line becomes energized from an operating error or a live conductor making contact. Bracket grounding 2 miles apart will provide protection from induction and backfeed from small generators."
The reply suggests that there is a difference between a reenergized line and a backfed or induced line. How does bracket grounds two miles apart protect me from backfeed or induction but not from the line being reenergized? It doesn't protect at all.
#33
Posted 31 May 2004 - 12:53 PM
A nearby power line will induce a voltage on a nearby isolated conductor. There is no current flowing in the isolated conductor if the isolated conductor is not part of a circuit. One set of protective grounds on an isolated circuit will collapse the voltage due to electric field induction. If a worker was to get between an isolated conductor and the earth, the exposure to the high induced voltage combined with the relatively small amount of current available could be fatal.
A nearby power line will induce current on a nearby isolated conductor when that conductor forms part of a circuit. Grounding a conductor on each side of a work zone (bracket grounding) will create a circuit through the conductor, down one set of grounds, through the earth and back up the other set of grounds. The first set of grounds installed on an isolated conductor will collapse the induced voltage from the electric field, a second set of grounds will create a circuit which will cause an induced current to flow from the magnetic field.
When bracket grounds are removed, the first set of grounds removed will open the circuit and interrupt the current flow. An immediate voltage will appear (recovery voltage) across the gap between the ground clamp and the conductor. In high induction areas a long arc could be drawn. When there are more sets of grounds installed along the line, it will be the second to last ground removed where there could be a long arc drawn.
Once bracket grounds are installed, the conductor between the two sets of grounds will have very little induced voltage but could have a high electrical current flowing through it. When grounds are installed at a work site (between the bracket grounds) the work site set of grounds will have relatively very little current flowing in it. The middle set of grounds creates two circuits for the ground current to flow where previously there was one. The current from one circuit goes up the middle set of grounds and the current from the other set of grounds goes down the set of grounds. The two currents tend to cancel out and, therefore, very little current flows in these grounds.
When working on an isolated circuit, protective grounds on the circuit will reduce the voltage due to backfeed from a small portable generator to an acceptable level. The transformer impedance and the resistance of the conductor between the grounds and the generator will probably not create a large enough fault current to cause the generator to overload. The generator will keep running, the grounds will bring the voltage down to a safe level, but there will be a current flow in the conductor. Because there is always a chance of current flow in a conductor, the conductor should not be cut or joined without first installing a jumper.
Backfeed from larger industrial or commercial generators would cause higher voltages to appear on grounded conductors at the work site. Large generators are more likely to be installed and inspected properly, so backfeed is very unlikely. The hazard from backfeed is from the unknown generator.
Meanwhile, while I am writing this I am thinking that I need to research this a little more. avatar233[1].gif say what
Wayne
#34
Posted 31 May 2004 - 02:16 PM
#35 Guest_TexasLineworker_*
Posted 31 May 2004 - 02:52 PM
One on the rig itself where the operator stands, the other on the ground where the operator would climb on or off the rig. The rig is also barricaded with flagging tape and cones to keep people from wanting to lean against it duing the stringing process. The operator is required to wear rubber gloves during the stringing process as well. And finally, the main rule to go by is to stay on the rig or off the rig, no jumping back and forth while stringing. Hope that helps ya partner!
brewsky
#36
Posted 02 March 2010 - 05:28 PM
#37
Posted 02 March 2010 - 05:50 PM
#38
Posted 17 May 2010 - 10:07 AM
CHANCE Grounding Encyclopedia
#39
Posted 26 October 2010 - 09:17 PM
Ep bonding is required in addition to temp working grounds on 66kv and below if any of these conditions apply:
-If you do not have two open points (a float installed and a fargo(hot line tap) removed)
-Cannot maintain adequate clearance from adjacent lines.
-Sources of induction are present
-If Low voltage sources of back feed cannot be eliminated
-If lightning is probable or occurring in the area