What does 'float' mean?
the terms
wye/wye you tie
wye/delta you float
refer to the tying to or floating the neutral on the high side of the transformer. so wye primary/wye secondary you tie the h1's or h2's, in your pics its the h1's, to the neutral. wye/delta you float, just connect them together. if that made sense???
Lrod, i dont see a primary neutral. so in what circumstance do you tie and when would you float on wye/delta? Is tying to the pole ground the same as tying to neutral if one was there?
Looks like there is a system neutral to me... looks like 6 or 4 copper.
It's a wye-delta bank, 3 phase 4 wire 120/240.
I'd go with a 99% probability that the wye is floated on top, you'd want to float the wye so that if one of the power pots fail the customer would see no voltage, otherwise if you grounded the wye the other power pot would carry all of the 3 phase load, potentially burning up the other power pot.
In any new installations here we use a 4th cutout to prevent ferroresence... even on older ones when we work on them we'll install the 4th cutout.
On a open wye-open delta bank you'd ground the wye, practice at my utility is to use single bushing transformers in that case instead of two bushing.
The only thing that is different is they used H2 on the primary instead of H1, all that did is change the polarity of each transformer... really no big deal, just make sure you do that on all three if all three are the same polarity.
The lighting pot with the 4 bushings, I've only seen one of them, but to my understanding it's just an external way of changing your coil to utilize if you wanted to cut it two wire for a 120/208 (or 277/480) application (A C B D).
Floating the wye just means lets say on this picture
Each pot has one phase of primary going into H2 ( A B C ) the other top bushing H1 just has a common lead going to each transformer... it just floats, only ties into each H2.
Here's a diagram of floating wye